Jump to content

more electrical stuff


Recommended Posts

ok. so we have just fully re-wired a house.

 

Two lighting circuits, giving off bad IR readings..... REALLY bad phase to earth was as low as .280MegOhm on a 500 setting

 

Useing a loop in, to the lights, ie; only one 1.5mm cable at switch's....except two way switch's, obviously.

 

Disconnect all the switch drops. test them individually.... P-N P-E & E-N ALL READ >1000Mohm on each of the switch drops.

 

We split the light circuit..... Go to end of line, so we're testing from bathroom light, through fan isolatotor and into bedroom1. Readings as above.

 

Then we test from bed 1, to bed 2, bed 3, and back down to the board. readings all >1000

 

Okay, everything has been tested. Just for good measure i zap another 500 from the board, through the lights....and get poor readings.......

 

How come we're getting poor readings one way, and good readings the other?

Link to post
Share on other sites

hello mate disconnect the fan and isolator and just make sure you havnt missed anything like dimmers etc we had a post office like that we were having a nightmare untill we found a fused spur under the counter feeding a fan

 

atb

 

nasher

Link to post
Share on other sites

yeah the earth's were disconnected.

 

Never though about disconnecting them from the fan spur. Although its in the "off" position, the earth will still be continuos right through the fan, yeah?

 

I'll be trying that first thing tommorow morning.

 

CHEERS

Link to post
Share on other sites
yeah the earth's were disconnected.

 

Never though about disconnecting them from the fan spur. Although its in the "off" position, the earth will still be continuos right through the fan, yeah?

 

I'll be trying that first thing tommorow morning.

 

CHEERS

 

all depends is it a fan switch like the 2 pole jobs??has it a fan icon on it ??u got pm for that 17th edition site

 

atb

 

nasher

Link to post
Share on other sites
I'm no sparky, but is is possible you have a reversed connection somewhere?

 

i dont think that would change it to be ok one way and it to be out on 'tother. if that was the problem though, it would of shown up on polarity check anyway.

Link to post
Share on other sites
I'm no sparky, but is is possible you have a reversed connection somewhere?

 

Appreciate your input, but no, there is nothing "reversed" :D

Well I did say I wasn't a sparky! :laugh: I was in the construction trade, and I've seen some stranger things though. I plastered this house once, and as it was nearing completion, the owner decided to test his boiler out. About half hour after the heating was turned on, his wife came running out of the toilet in fits of laughter. We went to have a look, didn't see nothing wrong at first, then she flushed the chain! It was the first time I've ever seen a hot flushing toilet! :laugh:

Link to post
Share on other sites

Is it PME ot tns or tnts ? Maybe that could account for it?

 

Are you using BASEC cable or cheap import carp, had a do with one once cheap import and was missing insulation on L & N in the same place when we stripped it.

Link to post
Share on other sites

its a T-N-S

 

when we do the ins. res. test, for example on a ring main, the two 2.5's are completely out the board, so i doubt that what sort of supply would make any difference.

 

We are using good cable, forgot the name of the stuff. But I've used it for years without problems.

 

cheers

Link to post
Share on other sites

Has damp had chance to get in i.e weeks before second fix/test is the place cold and damp?

 

To tell the truth I used to independantly test for the NICEIS and have had some strange readings from originals, without actually seeing the instalation and being able to see the r1+r2 and insulation readings its a bit confusing and dont want to add to your problems. Sorry.

Link to post
Share on other sites

gav. I'll give you the latest scenario.

 

!st & 2nd fixed up stairs ring yesterday (wednesday) and done the dead test's today.

 

From the board, i got L-N >1000 L-E 509 E-N 613 somewhere along those lines........

 

I disconnected a socket, approx half way round the circuit. so i test from the board to that socket, everything read >1000.

 

I test from that socket, round the rest of the installation. low readings....

 

I disconnected another socket further round. So i test between the two disconnected sockets. Then i test from the second dissconnected socket, back to the board. Both leg's came up fine (>1000 on each test)

 

I connect both sockets back, and then test again from the board, and get poor readings again.

 

It's baffling me.......... all the second fix work was good, because i went and re-done it all after our apprentice made a bad job of it.

 

Perhaps the problem lays in the actual sockets? Maybe worth testing them?

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
  • Recently Browsing   0 members

    No registered users viewing this page.

×
×
  • Create New...