I will add. I done a continuity test on between Phase & CPC.... and it came up with >1000ohms (open circuit) which is fine. But its just doing the Ins. Res. Tests when we get crap readings. R1-R2, Earth Fault Loop, Ring final continuit etc...... are all fine

Link to post
Share on other sites

gav. I'll give you the latest scenario.

 

!st & 2nd fixed up stairs ring yesterday (wednesday) and done the dead test's today.

 

From the board, i got L-N >1000 L-E 509 E-N 613 somewhere along those lines........

 

I disconnected a socket, approx half way round the circuit. so i test from the board to that socket, everything read >1000.

 

I test from that socket, round the rest of the installation. low readings....

 

I disconnected another socket further round. So i test between the two disconnected sockets. Then i test from the second dissconnected socket, back to the board. Both leg's came up fine (>1000 on each test)

 

I connect both sockets back, and then test again from the board, and get poor readings again.

 

It's baffling me.......... all the second fix work was good, because i went and re-done it all after our apprentice made a bad job of it.

 

Perhaps the problem lays in the actual sockets? Maybe worth testing them?

 

That sounds like a good idea mate, link it all out without any sockets inline, or maybe do an ins test on each socket. You are going about it the right way and its bloody annoying I know. I am pretty reluctant to give advice if I cant see the instalation as you will appreciate yourself, popping up with ideas will just add to your quandry.

 

Just an after thought : did you do the tests after screwing the sockets back or leaving them loose?

 

Let us know if you get to the bottom of it

Link to post
Share on other sites

sockets screwed back mate..... no insulation of any conductor caught,l i know, i screwed them back :D

 

much appreciated for info gav...

 

i think i'll be ins. res'ing the actual socket's tommorow.

 

All the ins tests are over 1ohm, thus complying with reg's.... i better start marking my test sheets with >200Mohms rather than >1000Mohms :D

 

cheers

RH

Link to post
Share on other sites
When was the last time your meter was calibrated?

 

A callibration is just a means of making sure it complies with the same readings as other test instruments and not if it working correctly! If it was not working correctly it would be quite apparent, not callibrated would mean it would not give the same readings as another intrument. I dont think this is an issue here.

Link to post
Share on other sites
sockets screwed back mate..... no insulation of any conductor caught,l i know, i screwed them back :D

 

much appreciated for info gav...

 

i think i'll be ins. res'ing the actual socket's tommorow.

 

All the ins tests are over 1ohm, thus complying with reg's.... i better start marking my test sheets with >200Mohms rather than >1000Mohms :D

 

cheers

RH

 

Screwing the sockets back does increase forces on internal components which if faulty could highlight these readings. Try an insulation test on a few sockets first then if you find no faults try linking the circuit with connectors without any thing inline, I would be suprised if the results all come back the same.

 

Good luck.

Link to post
Share on other sites

aint a clue oneredtrim.....

 

just tested a house today which another gang first fixed.... and had similar low readings.....

 

as you say the common denominator is the cable, the test meter..... AND.....our bloody apprentice !!

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
  • Recently Browsing   0 members

    No registered users viewing this page.

×
×
  • Create New...