I've finally got myself a decent little inverter welder. It runs on 13a ok, but I don't really "get" electrics.

 

I have a massive armoured power cable running to the garage which ends in a fuse board. From this there is 16a cable running to a cooker socket.

 

I use the 13a plug-in part of this socket, so I assume even though 16a is running to it, it's only 13a and apparently that's a bit marginal at the higher amps on the welder (160a).

 

Is this socket only 13a because it only takes a 13a plug?

 

As there is obviously no cooker in the garage (shame), would it make sense to run a 16a cable from the cooker socket and end it with a 16a socket like you get on caravans, and put the matching plug on the welder?

 

Or is there an easier solution? :hmm:

 

And no, it's not a townie question as townies have welders too. :laugh:

Link to post
Share on other sites

I don't know fook all about electric. I would Just plug it in and use it.

 

If the fuse keeps popping stop using it.

 

What's the worst thing that can happen :)

 

Apart from a fire or an explosion you mean?

 

It hasn't popped anything yet, but I've only been up to 120a.

 

I just thought I should or could make use of a 16a supply as there's one there.

Link to post
Share on other sites

You don't have to use all the power it can supply. For example some things have a 3a fuse on but plug in to a socket that had a 13a plug on before

 

If the welder is ment to take 13a then don't swap the end and give it 16a as it will die without the 13a fuse to save it..

  • Like 1
Link to post
Share on other sites

What size is the breaker/ fuse supplying the cooking socket (Normally they are fed at around 40 amp)? If it is a 16amp just remove the cooker socket and put a 16 amp socket on the end of the cable instead and the corresponding plug on the welder ( the caravan type you mentioned). What size supply does the welder actually need, it should say in the manual. Ps I'm a sparky by trade

ATB Andy

Link to post
Share on other sites

What size is the breaker/ fuse supplying the cooking socket (Normally they are fed at around 40 amp)? If it is a 16amp just remove the cooker socket and put a 16 amp socket on the end of the cable instead and the corresponding plug on the welder ( the caravan type you mentioned). What size supply does the welder actually need, it should say in the manual. Ps I'm a sparky by trade

ATB Andy

 

I'll check what size the breaker supplying it once I've traced it back and work out which one it is. The welder is American, so the instructions assume I am too. :laugh: It just says 1ph 230v.

 

Most other inverters say 160 amp requires a 16a supply, so I guess that's the same.

Link to post
Share on other sites

Inverter welders are funny old things and the supply varies between manufactuers but like you say 16A is the norm. It will be easier once you know the size of the breaker feeding the cooker socket as if it's bigger than 16amp, you don't really want to be putting a 16 amp socket on the end as you will be over rating it and have the potential for electrical fire/ damage (if the welder developed a fault.)

  • Like 1
Link to post
Share on other sites

Walshie, there is no such thing as a 16A cable fella!

 

The fuse protects the cable that follows it. So the breaker in your DB should be suitably rated to protect the cable that comes out of that and into you 'cooker outlet'.

 

If the welder comes with a standard 3 pin socket on rated at 13A, i.e. with a 13A fuse in it, DO NOT replace this with anything rated higher as this 13A fuse is to protect the flex from the plug to the bit of kit.

 

If however this is second hand and this plug has been fitted by someone for ease of use then you need to refer to manufacturers info for max load of the bit of kit.

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.